The right inverter for battery storage and some other Qs

Oldgreybeard
Posts: 1873
Joined: Thu Sep 09, 2021 3:42 pm
Location: North East Dorset

Re: The right inverter for battery storage and some other Qs

#91

Post by Oldgreybeard »

ducabi wrote: Wed Oct 05, 2022 10:44 pm
marshman wrote: Wed Oct 05, 2022 7:53 pm Page 18 of manual:

 If the HYD-ES inverter is faulty, manually change the switch to position 2. Grid will supply power to critical
load

and fig 18. (top of page 19)

Yes you need a changeover (bypass) switch to enable the critical loads if the inverter fails.
I didn't pay much attention to that section as I thought it wasn't relevant given I'm not running it in UPS mode.
So, if it stops working and I want full power from the grid then only option is to fully disconnect it?
Why would the inverter failing have any effect on the grid feed to the house?

The grid doesn't stop working when there is no sun, or the house batteries run too low.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
sharpener
Posts: 460
Joined: Fri May 20, 2022 10:42 am

Re: The right inverter for battery storage and some other Qs

#92

Post by sharpener »

ducabi wrote: Wed Oct 05, 2022 10:44 pm
marshman wrote: Wed Oct 05, 2022 7:53 pm Page 18 of manual:

 If the HYD-ES inverter is faulty, manually change the switch to position 2. Grid will supply power to critical
load

and fig 18. (top of page 19)

Yes you need a changeover (bypass) switch to enable the critical loads if the inverter fails.
I didn't pay much attention to that section as I thought it wasn't relevant given I'm not running it in UPS mode.
So, if it stops working and I want full power from the grid then only option is to fully disconnect it?
No, if the inverter goes down you should be OK though it would be wise to disconnect it with the much-discussed isolator.

I am surprised you don't want to use the 3kW UPS capability, in the event of a power cut this would be enough to run some lights, the freezer, a gas or oil boiler and an emergency socket for other small loads.

As has been pointed out upthread you would ideally fit this with a bypass switch so if the grid is up but the inverter is down you will be able manually to switch these circuits to the grid. Even better a relay/contactor in the new CU could do this automatically at much the same parts cost.
16 x 230W Upsolar panels S Devon, 4kW Steca, 3.9 MWh FITs/yr
8 x 405W Longi panels, 250/60 MPPT, 3.3 MWh/yr
Victron MultiPlus II-GX 48/5000/70-50
10.65 kWh Pylontec Force-L2
zappi 7kW EVCS
Villavent whole-house MVHR
5000l rainwater system
Vaillant 12kW HP
ducabi
Posts: 172
Joined: Sat Sep 10, 2022 5:32 pm

Re: The right inverter for battery storage and some other Qs

#93

Post by ducabi »

sharpener wrote: Thu Oct 06, 2022 10:27 am No, if the inverter goes down you should be OK though it would be wise to disconnect it with the much-discussed isolator.

I am surprised you don't want to use the 3kW UPS capability, in the event of a power cut this would be enough to run some lights, the freezer, a gas or oil boiler and an emergency socket for other small loads.

As has been pointed out upthread you would ideally fit this with a bypass switch so if the grid is up but the inverter is down you will be able manually to switch these circuits to the grid. Even better a relay/contactor in the new CU could do this automatically at much the same parts cost.
I do want the UPS functionality but wanted to cover 1 thing at a time.
So, what do I need to be able to use UPS? Just the bypass switch + earth rod?
sharpener
Posts: 460
Joined: Fri May 20, 2022 10:42 am

Re: The right inverter for battery storage and some other Qs

#94

Post by sharpener »

ducabi wrote: Wed Oct 05, 2022 10:44 pm
marshman wrote: Wed Oct 05, 2022 7:53 pm
Yes you need a changeover (bypass) switch to enable the critical loads if the inverter fails.
I didn't pay much attention to that section as I thought it wasn't relevant given I'm not running it in UPS mode.
I took this to mean what it says <I thought it wasn't relevant given I'm not running it in UPS mode>

Then you will need the earth rod, and a 30mA RCD on the output to the critical circuits because the 100mA one on the input isn't sufficient for shock protection. They need to be different to provide some level of fault discrimination.

You don't need the bypass switch (or relay), this is an option if you are worried about the inverter failing. I have manual changeover switches fitted because the whole house is on the UPS side. I might add an automatic relay for the freezer because of the remote likelihood of the inverter failing while I am on holiday.
16 x 230W Upsolar panels S Devon, 4kW Steca, 3.9 MWh FITs/yr
8 x 405W Longi panels, 250/60 MPPT, 3.3 MWh/yr
Victron MultiPlus II-GX 48/5000/70-50
10.65 kWh Pylontec Force-L2
zappi 7kW EVCS
Villavent whole-house MVHR
5000l rainwater system
Vaillant 12kW HP
Moxi
Posts: 2757
Joined: Sun Oct 31, 2021 3:46 pm

Re: The right inverter for battery storage and some other Qs

#95

Post by Moxi »

Nice and easy on the solis inverter - grid fail theres an auxiliary out which I got my sparky to connect to two outdoor IP65 sockets in the battery shed, so if the power fails I just run a brace of extension leads in through the cat flap and choc in the essential circuits ie the router and the TV for the boss and the kids.

I will consider the more sophisticated route if this power issue starts to become the norm over a few winters.

To all out there on electric alone don't forget the budget mini single ring gas burners and a pack of the aerosol can sized gas cartridges - like this

https://www.amazon.co.uk/Parkland%C2%AE ... 3788&psc=1

Link only shown as an example - we have a clone of this that we use on holiday for days out to give the kids a warm meal on the cooler days.

Mr Gus, you are normally a wiz at knowing the best price and vendor for things like this, do you have any recommendations?

Moxi
User avatar
nowty
Posts: 6534
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: The right inverter for battery storage and some other Qs

#96

Post by nowty »

Moxi wrote: Thu Oct 06, 2022 1:54 pm Nice and easy on the solis inverter - grid fail theres an auxiliary out which I got my sparky to connect to two outdoor IP65 sockets in the battery shed, so if the power fails I just run a brace of extension leads in through the cat flap and choc in the essential circuits ie the router and the TV for the boss and the kids.
Is it just me or is there something typically British about this, :lol:
"run a brace of extension leads in through the cat flap"
19.6kW PV > 117MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 34MWh generated
7 Other RE Coop's
105kWh EV storage
90kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 530 m3
Oldgreybeard
Posts: 1873
Joined: Thu Sep 09, 2021 3:42 pm
Location: North East Dorset

Re: The right inverter for battery storage and some other Qs

#97

Post by Oldgreybeard »

nowty wrote: Thu Oct 06, 2022 2:11 pm
Moxi wrote: Thu Oct 06, 2022 1:54 pm Nice and easy on the solis inverter - grid fail theres an auxiliary out which I got my sparky to connect to two outdoor IP65 sockets in the battery shed, so if the power fails I just run a brace of extension leads in through the cat flap and choc in the essential circuits ie the router and the TV for the boss and the kids.
Is it just me or is there something typically British about this, :lol:
"run a brace of extension leads in through the cat flap"
Not a lot different to our system!

I have a second small CU right next to the main one, that just runs the essential circuits and includes the changeover contactor needed to swap from grid power to backup power for those three circuits. One of the circuits is just a radial with a handful of sockets close to the consumer unit, so if we need to run something like the TV during a power cut then I just need to run an extension lead from one of those spare sockets.

The essential circuits include the lights, and as we have some lighting circuit power outlets dotted around (the small round pin ones) I can run some low power loads from those. This arrangement was easier than trying to use one or both of the rings as a part of the backup system. Main things we want running if the power goes off are the lights, the water pump and the internet, although during the last long power cut that went down, seems there is only around an hour or so of backup power in those roadside fibre cabinets now.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
sharpener
Posts: 460
Joined: Fri May 20, 2022 10:42 am

Re: The right inverter for battery storage and some other Qs

#98

Post by sharpener »

Moxi wrote: Thu Oct 06, 2022 1:54 pm Nice and easy on the solis inverter - grid fail theres an auxiliary out which I got my sparky to connect to two outdoor IP65 sockets in the battery shed, so if the power fails I just run a brace of extension leads in through the cat flap and choc in the essential circuits ie the router and the TV for the boss and the kids.

I will consider the more sophisticated route if this power issue starts to become the norm over a few winters.

To all out there on electric alone don't forget the budget mini single ring gas burners and a pack of the aerosol can sized gas cartridges
We experience several power cuts a year, mostly they are a few mins in the morning and again in afternoon while WPD are repairing cables or making new connections, and we get warning of them.

So it wouldn't be worth doing the wires through the cat flap stuff, take too long, fortunately the Victron switchover is seamless anyway.

Nor would it address the return from holiday, freezer full of rotting/re-frozen food scenario. Unfortunately I have no spare ways where I can install a DIN-rail-mounted contactor for automatic failover and virtually no panel space for another box.

In extremis we have my grandmother's old oil lamp, a full tank of kero and an Aga. This will save us a lot of battery capacity in the winter as cooking accounts for maybe 1/4 of daytime usage.
16 x 230W Upsolar panels S Devon, 4kW Steca, 3.9 MWh FITs/yr
8 x 405W Longi panels, 250/60 MPPT, 3.3 MWh/yr
Victron MultiPlus II-GX 48/5000/70-50
10.65 kWh Pylontec Force-L2
zappi 7kW EVCS
Villavent whole-house MVHR
5000l rainwater system
Vaillant 12kW HP
Caesium
Posts: 218
Joined: Mon Sep 06, 2021 9:01 pm
Location: Brighton

Re: The right inverter for battery storage and some other Qs

#99

Post by Caesium »

Do you use double pole changeover switches for this, or just switch the live?

Just thinking I should do this on my UPS consumer unit.. and get that earth rod :)
Oldgreybeard
Posts: 1873
Joined: Thu Sep 09, 2021 3:42 pm
Location: North East Dorset

Re: The right inverter for battery storage and some other Qs

#100

Post by Oldgreybeard »

Caesium wrote: Thu Oct 06, 2022 3:25 pm Do you use double pole changeover switches for this, or just switch the live?

Just thinking I should do this on my UPS consumer unit.. and get that earth rod :)
I used a double pole changeover contactor, but you need to switch both poles for safety, just in case something odd happens to the incoming neutral because of the fault that has caused the power cut. Not unknown for the incoming neutral to go to a high voltage when there's a fault somewhere.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter