The right inverter for battery storage and some other Qs

ducabi
Posts: 172
Joined: Sat Sep 10, 2022 5:32 pm

Re: The right inverter for battery storage and some other Qs

#191

Post by ducabi »

marshman wrote: Mon Nov 07, 2022 10:44 am Can you sketch an actual wiring diagram showing the incoming main, old consumer unit with feed to the inverter and also wiring to the new "mini" consumer unit? I ask because from my interpretation of your description it seems the new "mini" C.U. is connected to the EPS output of the inverter via the MCB, but the C.U. is also connected to the grid via the main switch and the "Henley" block. If so then this is totally wrong and dangerous as the inverter will try to backfeed into the grid in EPS mode when it must be isolated from it.

Apologies if I have misunderstood your description.
Instruction from electrician for EPS: switch off grid isolator (1) + switch on EPS switch (2) + switch off DP in New mini CU, and then EPS works. I tested it by switching off isolator next to the meter.

Diagram.
Inverter gets power from Main CU (through MCB 32 Type B behind RCD 63A, 30mA Type AC).
Then when it feeds mini CU through EPS it goes through MCB only and.
I'm not entirely sure how and WHY new mini CU is linked to main CU because there are too many cables to trace it.
Image
Oldgreybeard
Posts: 1873
Joined: Thu Sep 09, 2021 3:42 pm
Location: North East Dorset

Re: The right inverter for battery storage and some other Qs

#192

Post by Oldgreybeard »

Not sure that diagram is right, TBH. If the EPS for your inverter works in the same way as the one for my Sofar ME3000Sp, then it needs a changeover contactor to switch the maintained supplies from grid power to EPS power. This is key, as without it there is a serious risk that it might try to backfeed the grid, which is both dangerous (for those working to fix any outage) and will overload the inverter EPS output. This is the diagram from the ME3000SP manual that shows how the contactor needs to be wired:

Sofar EPS.jpg
Sofar EPS.jpg (61.94 KiB) Viewed 3093 times
I used a more compact 16A changeover contactor for my system, that fits within the maintained supply CU at the left (the treatment plant was being serviced when this photo was taken, hence the reason its RCBO is off):


Image

If your second CU is doing the same function as mine, supplying power to the maintained circuits that are on during a power cut, then the wiring needs to be similar. Not sure if it helps, but this is a detailed wiring diagram of that small CU on my system:

Backup CU wiring.jpg
Backup CU wiring.jpg (153.05 KiB) Viewed 3093 times
The key thing is that the only source of power to that essential circuits CU is from either the 20A RCBO in the main CU, or the inverter EPS output. There is no direct connection between it and the grid at all, and must not be, as the contactor is a key safety isolation device to stop the grid ever being back powered from the inverter.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
User avatar
Stinsy
Posts: 3544
Joined: Wed Jun 02, 2021 1:09 pm

Re: The right inverter for battery storage and some other Qs

#193

Post by Stinsy »

Am I right that you have a 16A changeover contactor protected by a 20A RCBO?
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
6x 2.4kWh Pylontech batteries (14.4kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Oldgreybeard
Posts: 1873
Joined: Thu Sep 09, 2021 3:42 pm
Location: North East Dorset

Re: The right inverter for battery storage and some other Qs

#194

Post by Oldgreybeard »

Stinsy wrote: Tue Nov 08, 2022 9:31 am Am I right that you have a 16A changeover contactor protected by a 20A RCBO?
Yes, but that's fine, as contactor ratings are long duration carry loads, their short duration carry load is a fair bit higher. That contactor is rated to carry 128A for 10s at 40°C, 40A for 30s at 40°C, so is OK with 20A B curve RCBO protection. (Edited to add:)This is from the datasheet for the contactor used:

Contactor rating.jpg
Contactor rating.jpg (46.63 KiB) Viewed 3070 times
These are the trip times for a 20A B curve RCBO with a 40A overload. It will trip after between 5 and 15 seconds at 40A, and the contactor is rated to carry 40A for 30 seconds at 40°C, so there is a safe enough margin IMHO:

B curve 40A trip times.jpg
B curve 40A trip times.jpg (35.23 KiB) Viewed 3061 times
Bit of a moot point, anyway, as the inverter can only output around 13A and can only draw about the same, plus there's a 16A MCB on both the grid and load circuits at the inverter end. Over current protection is mostly about protecting cables from overheating, anyway, and the lower rating of the RCBOs in the small CU looks after that If there were to be multiple overloads that didn't trip the small CU RCBOs then the 20A RCBO would trip within about 20 seconds at 40A, well within the 30s that the contactor will safely carry 40A for.
Last edited by Oldgreybeard on Tue Nov 08, 2022 10:41 am, edited 6 times in total.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
marshman
Posts: 615
Joined: Thu Jun 17, 2021 7:58 pm

Re: The right inverter for battery storage and some other Qs

#195

Post by marshman »

Which is why I queried it in my post. There is no change over switch and the EPS is feeding in to the CU via an MCB which is totally wrong and dangerous in that it is too easy for one of the isolators to be left on and the EPS feed into the grid. Also there has been no mention of the earthing situation.
ducabi
Posts: 172
Joined: Sat Sep 10, 2022 5:32 pm

Re: The right inverter for battery storage and some other Qs

#196

Post by ducabi »

marshman wrote: Tue Nov 08, 2022 9:45 am Which is why I queried it in my post. There is no change over switch and the EPS is feeding in to the CU via an MCB which is totally wrong and dangerous in that it is too easy for one of the isolators to be left on and the EPS feed into the grid. Also there has been no mention of the earthing situation.
I could be wrong but if I switch off grid feeding to inverter, then switch off main switch in mini CU, then by switching ON EPS switch everything stays outside of grid, isnt it?

Earthing was mentioned couple pages ago, straight after installation. Basically that electrician said it's not required because it will be supplied during blackout. But I will have earth rod installed by my other electrician.
Oldgreybeard
Posts: 1873
Joined: Thu Sep 09, 2021 3:42 pm
Location: North East Dorset

Re: The right inverter for battery storage and some other Qs

#197

Post by Oldgreybeard »

ducabi wrote: Tue Nov 08, 2022 10:14 am
marshman wrote: Tue Nov 08, 2022 9:45 am Which is why I queried it in my post. There is no change over switch and the EPS is feeding in to the CU via an MCB which is totally wrong and dangerous in that it is too easy for one of the isolators to be left on and the EPS feed into the grid. Also there has been no mention of the earthing situation.
I could be wrong but if I switch off grid feeding to inverter, then switch off main switch in mini CU, then by switching ON EPS switch everything stays outside of grid, isnt it?

Earthing was mentioned couple pages ago, straight after installation. Basically that electrician said it's not required because it will be supplied during blackout. But I will have earth rod installed by my other electrician.
From the diagram there doesn't seem to be anything isolating the grid from the mini CU, that seems to be permanently connected via the tails to the Henley block.

The electrician is wrong about the earthing, too. If you have the most common forms of UK supply, either TN-C-S/PME or TN-S, then the earth is provided via the incoming cable from the street. If there is a power cut then there is a very good chance that the earth provided via this cable will not exist, as very often the earth/neutral is the first conductor to break in the event of cable damage (because it's always on the outside of the supply cable, so the first bit to get cut through accidentally). If the supply is TN-C-S/PME, then you may be lucky and have the cable break on the supplier side of an intermediate earth electrode on the supply, but I don't think you can rely on that being the case.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
User avatar
nowty
Posts: 6348
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: The right inverter for battery storage and some other Qs

#198

Post by nowty »

ducabi wrote: Tue Nov 08, 2022 10:14 am I could be wrong but if I switch off grid feeding to inverter, then switch off main switch in mini CU, then by switching ON EPS switch everything stays outside of grid, isnt it?
Sorry I have not been following this very well.

Are you saying your going to manually enable the EPS on the inverter after isolating everything manually ?

i.e, the EPS will be disabled as the default position in normal operation.
18.7kW PV > 110MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 33MWh generated
7 Other RE Coop's
105kWh EV storage
90kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 530 m3
ducabi
Posts: 172
Joined: Sat Sep 10, 2022 5:32 pm

Re: The right inverter for battery storage and some other Qs

#199

Post by ducabi »

nowty wrote: Tue Nov 08, 2022 10:24 am Sorry I have not been following this very well.

Are you saying your going to manually enable the EPS on the inverter after isolating everything manually ?

i.e, the EPS will be disabled as the default position in normal operation.
Not sure if it matters whether EPS mode in inverter settings is enabled or disabled in this case but the procedure is to go to garage and start switching things OFF and ON. Otherwise EPS won't work.
I tested it by switching off isolator switch next to meter and without doing the above there is no power to any of the circuits.
Oldgreybeard
Posts: 1873
Joined: Thu Sep 09, 2021 3:42 pm
Location: North East Dorset

Re: The right inverter for battery storage and some other Qs

#200

Post by Oldgreybeard »

ducabi wrote: Tue Nov 08, 2022 10:30 am
Not sure if it matters whether EPS mode in inverter settings is enabled or disabled in this case but the procedure is to go to garage and start switching things OFF and ON. Otherwise EPS won't work.
I tested it by switching off isolator switch next to meter and without doing the above there is no power to any of the circuits.
The concern is that from your diagram, there is no way to ever isolate the maintained supply CU from the grid. When the EPS isolator switch is on then the inverter powers the grid, via the red arrows I've added to your diagram:

Edited wiring diagram.jpg
Edited wiring diagram.jpg (24.45 KiB) Viewed 3072 times
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
Post Reply