You need to worry about more than just the current carrying capacity of the cable! You need to account for Voltage rise and your local supply voltage.Oldgreybeard wrote: ↑Sun Oct 23, 2022 3:11 pmThe cable rating table you need to use is the one in the wiring regs, that rates 2.5mm² flex cable at an absolute maximum of 25A for single phase, 4mm² flex is rated at 32A maximum:dangermouse wrote: ↑Sun Oct 23, 2022 2:51 pmInverter is 3.6kW. Good point on the cable - 2.5mm² should be good for 32A in free air but it's a bit borderline (going on info from http://www.cable-ratings.co.uk/).Oldgreybeard wrote: ↑Sun Oct 23, 2022 12:39 pm If your inverter is rated at 3kW, then you may find that 4mm² cable is too big to fit the glands and terminals that easily. You will have to use 4mm² if using a 32A RCBO, as that's too high a current rating to protect 2.5mm² cable. Largest size RCBO that can be used to protect 2.5mm² cable is 20A.
Luckily, cable is cheap, and I only need a couple of metres, so if the 4mm² cable won't go into the inverter, I'll have to go for 2.5 and get a 20A RCBO. It would be an expensive mistake though to pick an RCBO with too low a rating, and find it trips out whenever the inverter ramps up. Although, being curve C makes that unlikely, you would hope.
Flex cable rating from the regs.jpg
Our Sofar is connected using a 20A RCBO, which is fine, as the maximum current normally (for 3kW) is slightly over 13A. A 3.6kW inverter could draw or supply about 15.6A, so still fine on a 20A RCBO.
Eg, my 3.6kW inverter could’ve been wired in 1.5mm² but I went 2 sizes bigger to 4mm² so that the inverter didn’t cut out on sunny days due to over Voltage condition.