Solis 5kW Hybrid inverter

NikoV6
Posts: 218
Joined: Thu Aug 11, 2022 6:42 am

Re: Solis 5kW Hybrid inverter

#11

Post by NikoV6 »

How does the inverter know to isolate itself from the grid during a power cut?
14Kw Mitsubishi Ecodan ASHP
22 x JA Solar 455W Mono Perc Half Cell Silvers
Solis 8.0Kw 5G Dual MPPT Inverter
13.5Kw Tesla Powerwall
Zappi 2 Charger
iBoost
marshman
Posts: 614
Joined: Thu Jun 17, 2021 7:58 pm

Re: Solis 5kW Hybrid inverter

#12

Post by marshman »

__
Last edited by marshman on Sun Jun 11, 2023 1:25 pm, edited 1 time in total.
User avatar
nowty
Posts: 5888
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: Solis 5kW Hybrid inverter

#13

Post by nowty »

I didn't do a full charge either as all the forecasts were giving me over confidence. :oops:

Its a bit better here, should make it through to the cheapslot but wont be record breaking. The satellite view shows much more extensive cloud elsewhere too. And more heading towards me. :cry:

Image
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 27MWh generated
6 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
openspaceman
Posts: 662
Joined: Mon Mar 21, 2022 7:37 pm

Re: Solis 5kW Hybrid inverter

#14

Post by openspaceman »

What a result to start off a PV experience. 19kWh in, battery from 50% to 83% and the rest into the car. 200W going in even now.

My system 50 miles north down to 60W and a day's production of 16kWh, 4kWh exported yet with nominally the same installed peak power.
Morso S11
FIT
16 Sharp PV panels facing WSW 4kW
Solarmax 4200S inverter
Non FIT
3 Canadian solar DC coupled 1.75kW facing SSE
Storage
Growatt SPA3000TL BL inverter ac coupled
Growatt GBLI6532 6.5kWh lithium phosphate battery
openspaceman
Posts: 662
Joined: Mon Mar 21, 2022 7:37 pm

Re: Solis 5kW Hybrid inverter

#15

Post by openspaceman »

NikoV6 wrote: Thu Mar 02, 2023 9:39 am How does the inverter know to isolate itself from the grid during a power cut?
My understanding is that the inverter continually tries to push the frequency over 50Hz but cannot as the grid is vast in comparison. If the grid disappears the frequency goes up and reaches a preset cut off point (around 52Hz I think) within a few milliseconds.
Morso S11
FIT
16 Sharp PV panels facing WSW 4kW
Solarmax 4200S inverter
Non FIT
3 Canadian solar DC coupled 1.75kW facing SSE
Storage
Growatt SPA3000TL BL inverter ac coupled
Growatt GBLI6532 6.5kWh lithium phosphate battery
NikoV6
Posts: 218
Joined: Thu Aug 11, 2022 6:42 am

Re: Solis 5kW Hybrid inverter

#16

Post by NikoV6 »

openspaceman wrote: Thu Mar 02, 2023 5:31 pm
NikoV6 wrote: Thu Mar 02, 2023 9:39 am How does the inverter know to isolate itself from the grid during a power cut?
My understanding is that the inverter continually tries to push the frequency over 50Hz but cannot as the grid is vast in comparison. If the grid disappears the frequency goes up and reaches a preset cut off point (around 52Hz I think) within a few milliseconds.
Thanks, does that make it G100 compliant??
14Kw Mitsubishi Ecodan ASHP
22 x JA Solar 455W Mono Perc Half Cell Silvers
Solis 8.0Kw 5G Dual MPPT Inverter
13.5Kw Tesla Powerwall
Zappi 2 Charger
iBoost
User avatar
nowty
Posts: 5888
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: Solis 5kW Hybrid inverter

#17

Post by nowty »

NikoV6 wrote: Fri Mar 03, 2023 9:56 am
openspaceman wrote: Thu Mar 02, 2023 5:31 pm
NikoV6 wrote: Thu Mar 02, 2023 9:39 am How does the inverter know to isolate itself from the grid during a power cut?
My understanding is that the inverter continually tries to push the frequency over 50Hz but cannot as the grid is vast in comparison. If the grid disappears the frequency goes up and reaches a preset cut off point (around 52Hz I think) within a few milliseconds.
Thanks, does that make it G100 compliant??
No, G98 or G99 (like the older G83 and G59) is the standard which includes isolating itself from the grid in the event of a power cut.

G100 is the standard about export limitation to the grid.
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 27MWh generated
6 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
marshman
Posts: 614
Joined: Thu Jun 17, 2021 7:58 pm

Re: Solis 5kW Hybrid inverter

#18

Post by marshman »

NikoV6 wrote: Fri Mar 03, 2023 9:56 am
openspaceman wrote: Thu Mar 02, 2023 5:31 pm
NikoV6 wrote: Thu Mar 02, 2023 9:39 am How does the inverter know to isolate itself from the grid during a power cut?
My understanding is that the inverter continually tries to push the frequency over 50Hz but cannot as the grid is vast in comparison. If the grid disappears the frequency goes up and reaches a preset cut off point (around 52Hz I think) within a few milliseconds.
Thanks, does that make it G100 compliant??
Your Solis is G100 certified -a copy of the certificate is here:

https://midsummerwholesale.co.uk/pdfs/s ... 0-cert.pdf
sharpener
Posts: 436
Joined: Fri May 20, 2022 10:42 am

Re: Solis 5kW Hybrid inverter

#19

Post by sharpener »

openspaceman wrote: Wed Mar 01, 2023 10:25 pm
Well I hope they set it up to be largely self tending as she does not have time to faff about with it.

I would like a bit of information about preventing the pylontech from discharging when the EV is charging off peak.
The zappi instructions here mention this on pp 26 and 48 (not 52) but in the context of which gets priority for daytime generation so not really an answer.

As a starting point you would need to set the zappi to have an export margin of 100W i.e. the hybrid inverter needs to be exporting 100W before the zappi will start to charge but this is not in itself sufficient. There is a good myenergi discussion forum here. In particular the links at the beginning of this thread will perhaps give some guidance.

In my own system I had already installed a separate bypass switch for the garage so it is simplest to switch that to GRID before setting the car to charge overnight.
16 x 230W Upsolar panels S Devon, 4kW Steca, 3.9 MWh FITs/yr
8 x 405W Longi panels, 250/60 MPPT, 3.3 MWh/yr
Victron MultiPlus II-GX 48/5000/70-50
10.65 kWh Pylontec Force-L2
zappi 7kW EVCS
Villavent whole-house MVHR
5000l rainwater system
Vaillant 12kW HP
openspaceman
Posts: 662
Joined: Mon Mar 21, 2022 7:37 pm

Re: Solis 5kW Hybrid inverter

#20

Post by openspaceman »

Thanks, it is early days yet so hopefully she will be able to charge the car from PV for most of the summer, which gives me a little time to look into it.

I had hoped it would be a simple matter of setting the Zappi and battery to charge at the same time, maybe staggering the start of the battery till after the zappi had charged the car.
Morso S11
FIT
16 Sharp PV panels facing WSW 4kW
Solarmax 4200S inverter
Non FIT
3 Canadian solar DC coupled 1.75kW facing SSE
Storage
Growatt SPA3000TL BL inverter ac coupled
Growatt GBLI6532 6.5kWh lithium phosphate battery
Post Reply