Dreaded E031 error again......

#1

Post by ecogeorge »

My original Power one Aurora Pvi 3.6 solar inverter has the dreaded E031 again (repaired seveeral yrs ago) .
Replacement Ginlong fitted today but wish to repair again as a spare.
I can find someone to solder but can't remember where i got the last components,.- anyone got any ideas before i let google search ?
George
Image

Image

Image
1750w Vertical PV micro inverters
3800w almost horizontal/south
Aarrow Becton 7 Woodburner
Dream 3kw ASHP only connected to summer Pool.
Allotment heavy clay.
1.784kw Kirk Hill
0.875kw Derril Water
0.2kwWhitelaw Brae
1kw Harlow Hydro.
ecogeorge
Posts: 401
Joined: Sun Oct 31, 2021 7:23 pm
Location: Gloucestershire

Re: Dreaded E031 error again......

#2

Post by ecogeorge »

Save your time -just found on auction site for £2.68 each.
Two have burnt pcb -should I replace all?
George
1750w Vertical PV micro inverters
3800w almost horizontal/south
Aarrow Becton 7 Woodburner
Dream 3kw ASHP only connected to summer Pool.
Allotment heavy clay.
1.784kw Kirk Hill
0.875kw Derril Water
0.2kwWhitelaw Brae
1kw Harlow Hydro.
ecogeorge
Posts: 401
Joined: Sun Oct 31, 2021 7:23 pm
Location: Gloucestershire

Re: Dreaded E031 error again......

#3

Post by ecogeorge »

Have also had low internal battery message for several years :o - Assume its this one ? If i remove and replace will i lose any data/settings/ ??
George
Image
1750w Vertical PV micro inverters
3800w almost horizontal/south
Aarrow Becton 7 Woodburner
Dream 3kw ASHP only connected to summer Pool.
Allotment heavy clay.
1.784kw Kirk Hill
0.875kw Derril Water
0.2kwWhitelaw Brae
1kw Harlow Hydro.
ALAN/ALAN D

Re: Dreaded E031 error again......

#4

Post by ALAN/ALAN D »

Have repaired a few over the years.

Its a printed circuit board design fault where the plated through hole / surface area is not big enough to pass the current.
The old relays were taken apart and no signs of internal contact damage were seen.
Before inserting the relay pass multiple copper cables though the two current contact holes. Bend it both sides. Solder a circular cable round the top side. under the relay. Extend the P.C.B. side cables a few mm. in various directions. Insert relay. Solder a nice circular blob over the bits off copper / board track.

Never had on fail after repair. :D

https://www.rapidonline.com/Zettler-Ele ... gLRBfD_BwE
ecogeorge
Posts: 401
Joined: Sun Oct 31, 2021 7:23 pm
Location: Gloucestershire

Re: Dreaded E031 error again......

#5

Post by ecogeorge »

Alan - have sent you 2 x PM's but they show as in outbox ?? when I hover over them they say sent ??
Have you received ?
Sorry to ask publicly but thinking they haven't sent............
George
1750w Vertical PV micro inverters
3800w almost horizontal/south
Aarrow Becton 7 Woodburner
Dream 3kw ASHP only connected to summer Pool.
Allotment heavy clay.
1.784kw Kirk Hill
0.875kw Derril Water
0.2kwWhitelaw Brae
1kw Harlow Hydro.
ALAN/ALAN D

Re: Dreaded E031 error again......

#6

Post by ALAN/ALAN D »

Hello George
No problem. Can repair and test.
Can you send an Email to
alan.downing@homecall.co.uk

Regards
Alan
ALAN/ALAN D

Re: Dreaded E031 error again......

#7

Post by ALAN/ALAN D »

The ZETTLER 30 Amp relays by design. ????
Have a very small diameter contact supply cable. The average relay rated at that current
has got connection diameter cable / surface area considerably bigger.
I have been very happy with the AURORA inverters over the years.
I do find it strange it got to production with this type of relay fitted.
I did have one fail on my 6kW wind turbine. That was beyond repair. :oops:
The whole printed circuit board caught fire. They stopped selling the 6kW one.