LIPO Battery round trip losses

#1

Post by Andy »

This may be of interest for people planning storage. From my last years figures I am experiencing an average of around 23% loss in the round trip. This a Pylontech/Quattro/VictronMPPT combo. I was often charging and discharging at max power during the summer.
User avatar
AlBargey
Posts: 202
Joined: Mon Oct 11, 2021 8:41 pm

Re: LIPO Battery round trip losses

#2

Post by AlBargey »

Andy wrote: Sat Oct 21, 2023 3:43 pm This may be of interest for people planning storage. From my last years figures I am experiencing an average of around 23% loss in the round trip. This a Pylontech/Quattro/VictronMPPT combo. I was often charging and discharging at max power during the summer.
That's not good!

I get just under a 22% loss / 78% round trip efficiency with old FLA cells: Hoppecke, Quattro, Victron MPPTS's

My totals since installing a SmartShunt:

Image

Image

I also set up a Pylon, Multi, Victron MPPT system for a houseboat only really used for weekends, so it's not a very efficient system with the constant Multi base load, and they get 84% round trip.

Image

Image

I asked peoples round trip efficiencies a while ago on the Victron forum, and some people were getting closer to 90-98% with LiFePo4!
38m Barge, Solar (10.6 kWp), 26 kWh of LFP, 50kWh Akvaterm Thermal Store (750l)
Victron Quattro 8 kVA, CerboGX, 3,500L STP, 57kVa Perkins
Our live data: https://vrm.victronenergy.com/installat ... e/c76c4bf6
openspaceman
Posts: 662
Joined: Mon Mar 21, 2022 7:37 pm

Re: LIPO Battery round trip losses

#3

Post by openspaceman »

So is that what a smart shunt does, logs what goes in and what comes out? On the DC side?
Morso S11
FIT
4kW panels facing WSW
Solarmax 4200S

Non FIT
disparate string
1.75kW facing SSE
0.85kW facing NE

2.6kW facing WSW

Sunsynk 3.6kW inverter

Storage
10.4kWh GLS lithium phosphate battery
User avatar
nowty
Posts: 6440
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: LIPO Battery round trip losses

#4

Post by nowty »

It really depends exactly what you are measuring and whether your DC coupled or AC coupled. Some people are only measuring DC in to DC out. Some people measure DC in to AC out. And some are measuring AC in to AC out.

My old 24V Lead acid system measuring AC in to AC out was only 67.4% efficient. My latest 48V system with lithium is similar to what Andy is getting at high 70’s % on the full round trip. But even on my old system with LA the DC to DC round trip was 90.5%.

Image


DC to AC efficiency can be very poor if just running low power background base loads most of the year.
Image
19.6kW PV > 114MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 34MWh generated
7 Other RE Coop's
105kWh EV storage
90kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 530 m3
User avatar
Krill
Posts: 445
Joined: Fri Sep 02, 2022 4:38 pm

Re: LIPO Battery round trip losses

#5

Post by Krill »

I've been wondering about this for a while, most specifically the most efficient rate to discharge the batteries, and charge from the grid over night.

I figured from the curves it was in the 25% to 40% range and this is another potential benefit to having paralleled inverters. Just need to best way to make one inverter work up to 40% and then kick in the second inverter...
Solar PV: 6.4kW solar PV (Eurener MEPV 400W*16)
PV Inverter: Solis 6kW inverter
Batteries: 14.4kWh LiFePO4 batteries (Pylontech US5000*3)
Battery Inverter: LuxPowertek 3600 ACS*2
EV: Hyundai Kona 65kWh
WBS: 8kW Hunter Avalon 6 Multifuel burner (wood only)