Balcony solar PV

User avatar
Joeboy
Posts: 8109
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: Balcony solar PV

#601

Post by Joeboy »

openspaceman wrote: Thu Nov 16, 2023 3:54 pm What would be the position if it were brought in as hand luggage, could you pay the 20% VAT at customs?

Can these things be connected, lawfully, to the UK electricity network yet?
Big boy lederhosen on. Buy it, backpack it through, deal with aftermath later. Of which there will be none with regards to vat or connection repercussions.
Just one interpretation on this multifaceted subject. Envelopes are there to be pushed.

If I was uncomfortable with any of the above I wouldn't go there but then again I think MCS is a load of :fan: without the fan and I like deciding for myself on local star energy use.

Off to the beer festival OSM? 👌 :twisted:
Last edited by Joeboy on Thu Nov 16, 2023 11:49 pm, edited 1 time in total.
19.7kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
richbee
Posts: 603
Joined: Tue Apr 19, 2022 3:39 pm
Location: Northumberland

Re: Balcony solar PV

#602

Post by richbee »

Joeboy wrote: Thu Nov 16, 2023 11:18 pm
openspaceman wrote: Thu Nov 16, 2023 3:54 pm What would be the position if it were brought in as hand luggage, could you pay the 20% VAT at customs?

Can these things be connected, lawfully, to the UK electricity network yet?
Big boy lederhosen on. Buy it, backpack it through, deal with aftermath later. Of which there will be none with regards to vat or connection repercussions.
Just one interpretation. Envelopes are there to be pushed.

If I was uncomfortable with any of the above I wouldn't go there but then again I think MCS is a load of :fan: without the fan and I like deciding for myself on local star energy use.

Off to the beer festival OSM? 👌
Shame I don't get to go to Germany with work these days, or I could bring one back
Solar PV since July '22:
5.6kWp east/west facing
3.6kW Sunsynk hybrid inverter
2x 5.12kWh Sunsynk batteries
1.6kWp Hoymiles East/West facing PV on the man cave
Ripple DW 2kW
Ripple WB 200W
User avatar
Joeboy
Posts: 8109
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: Balcony solar PV

#603

Post by Joeboy »

richbee wrote: Thu Nov 16, 2023 11:48 pm
Joeboy wrote: Thu Nov 16, 2023 11:18 pm
openspaceman wrote: Thu Nov 16, 2023 3:54 pm What would be the position if it were brought in as hand luggage, could you pay the 20% VAT at customs?

Can these things be connected, lawfully, to the UK electricity network yet?
Big boy lederhosen on. Buy it, backpack it through, deal with aftermath later. Of which there will be none with regards to vat or connection repercussions.
Just one interpretation. Envelopes are there to be pushed.

If I was uncomfortable with any of the above I wouldn't go there but then again I think MCS is a load of :fan: without the fan and I like deciding for myself on local star energy use.

Off to the beer festival OSM? 👌
Shame I don't get to go to Germany with work these days, or I could bring one back
I am heading over next May... Might just go shopping for the sheer damn of it.
19.7kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Jinx
Posts: 80
Joined: Tue Sep 20, 2022 10:16 pm

Re: Balcony solar PV

#604

Post by Jinx »

Just stick a plug on a standard 2kW growatt, seems far cheaper than the dedicated balcony setups kW/£?
Meets DNO requirements with documents available.
chris_n
Posts: 165
Joined: Sun Jun 26, 2022 9:33 am

Re: Balcony solar PV

#605

Post by chris_n »

Jinx wrote: Fri Nov 17, 2023 7:11 am Just stick a plug on a standard 2kW growatt, seems far cheaper than the dedicated balcony setups kW/£?
Meets DNO requirements with documents available.
While not compliant with regs having a plug on an 800W inverter is unlikely to cause a problem, sticking a plug on a 2kw inverter shouldn't be contemplated for the reasons mentioned earlier.
Living the dream in Austria.
Uk property 3.75kW PV linked to 3kW inverter.
User avatar
Joeboy
Posts: 8109
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: Balcony solar PV

#606

Post by Joeboy »

chris_n wrote: Fri Nov 17, 2023 7:16 am
Jinx wrote: Fri Nov 17, 2023 7:11 am Just stick a plug on a standard 2kW growatt, seems far cheaper than the dedicated balcony setups kW/£?
Meets DNO requirements with documents available.
While not compliant with regs having a plug on an 800W inverter is unlikely to cause a problem, sticking a plug on a 2kw inverter shouldn't be contemplated for the reasons mentioned earlier.
Indeed. An overload risk I personally wouldn't contemplate.
From a potential 3.3A to 8.3A isn't leaving much headroom on an already populated circuit.
19.7kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
AE-NMidlands
Posts: 2034
Joined: Wed Jun 02, 2021 6:10 pm

Re: Balcony solar PV

#607

Post by AE-NMidlands »

Joeboy wrote: Fri Nov 17, 2023 7:28 am Indeed. An overload risk I personally wouldn't contemplate.
From a potential 3.3A to 8.3A isn't leaving much headroom on an already populated circuit.
But if your "delivering" plug is somewhere on a ring main then surely it will reduce the current rather than increase it? If you could safely have put an applience drawing 13A in the same socket, then how can putting 8A into the circuit reduce the headroom? 4A might "flow each way" from the socket, so that must be 4A less each way from the consumer unit.
Or is this too simplistic an explanantion?
A
2.0 kW/4.62 MWh pa in Ripples, 4.5 kWp W-facing pv, 9.5 kWh batt
30 solar thermal tubes, 2MWh pa in Stockport, plus Congleton and Kinlochbervie Hydros,
Most travel by bike, walking or bus/train. Veg, fruit - and Bees!
User avatar
Joeboy
Posts: 8109
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: Balcony solar PV

#608

Post by Joeboy »

AE-NMidlands wrote: Fri Nov 17, 2023 8:41 am
Joeboy wrote: Fri Nov 17, 2023 7:28 am Indeed. An overload risk I personally wouldn't contemplate.
From a potential 3.3A to 8.3A isn't leaving much headroom on an already populated circuit.
But if your "delivering" plug is somewhere on a ring main then surely it will reduce the current rather than increase it? If you could safely have put an applience drawing 13A in the same socket, then how can putting 8A into the circuit reduce the headroom? 4A might "flow each way" from the socket, so that must be 4A less each way from the consumer unit.
Or is this too simplistic an explanantion?
A
Damn good question and one i'm not qualified to answer. I like to keep things simple. Too complicated for my little brain to think in millisecond responses of breakers, momentary loads, circuit resistance, partial or complete ring mains. I just do a simple Amps chimney sum and think OK or nope, not going there. :xx:

There is also a part of me that thinks 'well, the Germans checked it out and ok'd it to 800W, should be good'. In the case of the Hoymiles it is a fused double plug with a 5A fuse within and on a short spur back to the CU. I say this last as its important to emphasise for anyone passing through that all our homes are unique. Some due diligence has to be carried out. Personally, I don't like the idea that a daftie could put multiple micros on the same circuit but when you stick a plug on it and DIY it, that door opens. No disrespect to Jinx but a 3 pin 13A plug on a 2kW inverter? That is a little too much load/heat/risk of arc for my wee RA matrix. Fair play to anyone that does it, photos please. :D
19.7kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
richbee
Posts: 603
Joined: Tue Apr 19, 2022 3:39 pm
Location: Northumberland

Re: Balcony solar PV

#609

Post by richbee »

As I am also looking at a similar issue, I did a quick web search.
One answer which seemed to make sense is that if your ring main has a 32A breaker on it - if you have multiple sockets, and you run kettles, toasters, hairdryers etc etc at the same time, your breaker will trip if you go over 32A, which will protect the 2.5mm cable from overheating and worst case melting.
If you add 8A of solar to the mix, you could then run 40A of load through the ring main before the breaker would see 32A and trip, therefore making the circuit potentially more dangerous.
Solar PV since July '22:
5.6kWp east/west facing
3.6kW Sunsynk hybrid inverter
2x 5.12kWh Sunsynk batteries
1.6kWp Hoymiles East/West facing PV on the man cave
Ripple DW 2kW
Ripple WB 200W
chris_n
Posts: 165
Joined: Sun Jun 26, 2022 9:33 am

Re: Balcony solar PV

#610

Post by chris_n »

As richbee says the problem is adding extra current into a ring main which contains 2.5mm cable and is fused at 32A. If you add another 8A that does not flow through the overload protection device then you have 40A available at certain points in the circuit. So far you may think that's not really a problem but now consider if there is a break in the ring which could (more than likely would) go undetected then you are putting 40A into a single 2.5mm cable.
Joeboy makes a point about the Germans thinking 800W is ok but this is only part of the story. Germany as well as the rest of Europe don't use ring mains, they use radial circuits fused at 20A so the max you would see there would be 23.3A with an 800W inverter.
Living the dream in Austria.
Uk property 3.75kW PV linked to 3kW inverter.