LuxPower - emergency backup enabling

marshman
Posts: 614
Joined: Thu Jun 17, 2021 7:58 pm

Re: LuxPower - emergency backup enabling

#41

Post by marshman »

__
Last edited by marshman on Sun Jun 11, 2023 2:46 pm, edited 1 time in total.
openspaceman
Posts: 662
Joined: Mon Mar 21, 2022 7:37 pm

Re: LuxPower - emergency backup enabling

#42

Post by openspaceman »

Okay, staying with the subject of small generators and slightly derailing; if the house is islanded and earthing by an earth spike, running a normal consumer unit, will the RCDs still react to a L to E fault if the generator is not earthed? Logically a circuit cannot complete so the RCD will not see the inbalance
Morso S11
FIT
16 Sharp PV panels facing WSW 4kW
Solarmax 4200S inverter
Non FIT
3 Canadian solar DC coupled 1.75kW facing SSE
Storage
Growatt SPA3000TL BL inverter ac coupled
Growatt GBLI6532 6.5kWh lithium phosphate battery
Oldgreybeard
Posts: 1873
Joined: Thu Sep 09, 2021 3:42 pm
Location: North East Dorset

Re: LuxPower - emergency backup enabling

#43

Post by Oldgreybeard »

openspaceman wrote: Tue Oct 18, 2022 11:59 am Okay, staying with the subject of small generators and slightly derailing; if the house is islanded and earthing by an earth spike, running a normal consumer unit, will the RCDs still react to a L to E fault if the generator is not earthed? Logically a circuit cannot complete so the RCD will not see the inbalance
Simple answer is that for the RCDs to be guaranteed to operate within their specs for time and current, then two things need to be present. First is that neutral and earth must be linked at the generator, second is that the earth electrode resistance must be low enough to ensure that the 30mA earth leakage trip current can be reached without the voltage on the earthed equipment exposed conductive parts exceeding 50V (the safe touch voltage).

To meet both these requirements just means connecting earth to neutral at the generator (taking note of the uncertainty about generator configurations mentioned earlier) and having an earth electrode providing the protective earth that has a resistance (Ra) that is lower than 1,667 ohms. In reality, although 1,667 ohms is safe, the guidance is that the value of Ra should be lower than 200 ohms when measured at the time of installation. The reason for the lower value is to allow for natural variation in earth electrode resistance with the weather (they go low in very wet weather, higher in very dry weather).
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
openspaceman
Posts: 662
Joined: Mon Mar 21, 2022 7:37 pm

Re: LuxPower - emergency backup enabling

#44

Post by openspaceman »

So a simple test is to open the 3 pin shutter of the generator output when it is not running and measure resistance between N and E? If Near 0 Ohms bond E to earth spike?
Morso S11
FIT
16 Sharp PV panels facing WSW 4kW
Solarmax 4200S inverter
Non FIT
3 Canadian solar DC coupled 1.75kW facing SSE
Storage
Growatt SPA3000TL BL inverter ac coupled
Growatt GBLI6532 6.5kWh lithium phosphate battery
Oldgreybeard
Posts: 1873
Joined: Thu Sep 09, 2021 3:42 pm
Location: North East Dorset

Re: LuxPower - emergency backup enabling

#45

Post by Oldgreybeard »

openspaceman wrote: Tue Oct 18, 2022 12:56 pm So a simple test is to open the 3 pin shutter of the generator output when it is not running and measure resistance between N and E? If Near 0 Ohms bond E to earth spike?
Yes, that would be an OK check to do.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
stevevoller
Posts: 6
Joined: Sat Jan 06, 2024 6:54 pm

Re: LuxPower - emergency backup enabling

#46

Post by stevevoller »

I am not an electrical engineer so please excuse me if this is a stupid question.

I have a Luxpower ACS 3600 and Growatt min 6000 (with 5.4KW PV) that are AC connected to the house and grid.

The PV powers the house load, them charges the battery and if anything is left exports to the grid.

Is it possible when a power cut occurs to have the system switch to powering the house from the EPS, whilst keeping the PV powering the house and charging the battery.

From what I have read in the manual the normal operation would be to have the EPS (powered by battery only) drive a separate consumer unit with specific parts of the house load.

This seems really poor use of the system and will fail once the battery is expired. I understand the safety reason for turning off the output of the inverters when they are grid connected.

But is it possible to somehow have a transfer switch that will disconnect the grid and connect the EPS to the house load? whilst also allowing the use of the use of the PV?

I read and partially understood the long thread about Earthing, if we had a separate earth for the house installed is that ok?
Tinbum
Posts: 1073
Joined: Mon May 31, 2021 9:55 pm

Re: LuxPower - emergency backup enabling

#47

Post by Tinbum »

No you can't run the pv inverter off the eps as the eps circuit can't charge the battery.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
User avatar
Stinsy
Posts: 2640
Joined: Wed Jun 02, 2021 1:09 pm

Re: LuxPower - emergency backup enabling

#48

Post by Stinsy »

stevevoller wrote: Sat Jan 06, 2024 9:19 pm I am not an electrical engineer so please excuse me if this is a stupid question.

I have a Luxpower ACS 3600 and Growatt min 6000 (with 5.4KW PV) that are AC connected to the house and grid.

The PV powers the house load, them charges the battery and if anything is left exports to the grid.

Is it possible when a power cut occurs to have the system switch to powering the house from the EPS, whilst keeping the PV powering the house and charging the battery.

From what I have read in the manual the normal operation would be to have the EPS (powered by battery only) drive a separate consumer unit with specific parts of the house load.

This seems really poor use of the system and will fail once the battery is expired. I understand the safety reason for turning off the output of the inverters when they are grid connected.

But is it possible to somehow have a transfer switch that will disconnect the grid and connect the EPS to the house load? whilst also allowing the use of the use of the PV?

I read and partially understood the long thread about Earthing, if we had a separate earth for the house installed is that ok?
1) The Lux has a UPS not an EPS function. EPS is powered only in an outage, UPS is always powered.

2) You could totally have a changeover switch that swapped the whole house from grid to UPS circuits. But doing so wouldn’t be a good idea. Better would be to have one dedicated sockets circuit and maybe your lighting on the UPS circuit.

3) There are some very important earthing issues to resolve if using the UPS circuit.
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
stevevoller
Posts: 6
Joined: Sat Jan 06, 2024 6:54 pm

Re: LuxPower - emergency backup enabling

#49

Post by stevevoller »

Thank you for the reply it is appreciated, I am just trying to understand enough so I can explain enough to the electricians as to how I would like things to work.

(I went back and read the manual for the ACS 3600 and you are correct it does say UPS)

Where are you suggesting the placement of the manual transfer switch in the system ?

What I don't understand is in the event of a power cut and the manual transfer switch being used, what am I switching?
1. The separate "UPS" consumer unit from main AC to UPS on ACS3600? That would leave the Growatt PV, output from the ACS3600 and rest of the house still connected to the grid in an off state..
2. Something else?

Is there a way to keep the solar inverter on so at least some of the remaining house load and potentially battery can be charged?

Am I asking too much for a standard home install, should I just give up and get some kind of hybrid inverter?

At the moment I have everything quite optimised except for power cuts which are a bit to frequent.
1. PV powers house first,
2. if excess PV and battery is not fully charged, then charges battery,
3. if battery is fully charged and car is plugged in then send excess PV to the Zappi charger,
4. and finally the export to grid.
Tinbum
Posts: 1073
Joined: Mon May 31, 2021 9:55 pm

Re: LuxPower - emergency backup enabling

#50

Post by Tinbum »

The problem is that if the solar inverter is producing more than the house load and the battery is full the LUX has to be able to tell the PV inverter to throttle back. If it can't then you have problems. I don't believe it has that facility and can't accept power in on the output..

You may be able to do it but would have to have automatic loads come on.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
Post Reply