Hi
I have 6 Pylontech 2000 batteries in a single stack with a Lux LXP 3600 ACS inverter.
I also have 4 Pylontech 2000C batteries that are waiting for a second installation on a different phase that has been significantly delayed.
Can you connect 10 Pylontech batteries in a single stack? I cannot seem to find a definitive answer in the manual or on line.
I an thinking of adding the 4 as a temporary connection to the original stack rather than leaving them unused and maybe deteriorating.
Ian
Maximum Pylontech 2000 batteries in a single stack?
Re: Maximum Pylontech 2000 batteries in a single stack?
The non 'C' types can only have 8 in a stack unless you buy an expensive pylotech hub.
The 'C' types can have 16 in a stack.
But, you can make the master (number 1) a US2000C and number 9 and 10 in the stack a US2000C. The non 'C' types (and the forth 'C' type) can be numbers 2 to 8.
The 'C' types can have 16 in a stack.
But, you can make the master (number 1) a US2000C and number 9 and 10 in the stack a US2000C. The non 'C' types (and the forth 'C' type) can be numbers 2 to 8.
16.9kW PV > 107MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 22MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Ripple 6.6kW Wind + 4.5kW PV > 22MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Re: Maximum Pylontech 2000 batteries in a single stack?
It is in the manual.bpabpa wrote: ↑Wed Jan 31, 2024 3:43 pm Hi
I have 6 Pylontech 2000 batteries in a single stack with a Lux LXP 3600 ACS inverter.
I also have 4 Pylontech 2000C batteries that are waiting for a second installation on a different phase that has been significantly delayed.
Can you connect 10 Pylontech batteries in a single stack? I cannot seem to find a definitive answer in the manual or on line.
I an thinking of adding the 4 as a temporary connection to the original stack rather than leaving them unused and maybe deteriorating.
Ian
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
Re: Maximum Pylontech 2000 batteries in a single stack?
Thanks for the response.