Sofar ME3000 Emergency output
Sofar ME3000 Emergency output
Quick question - does anyone know if I can configure the ME3000 battery system so that the Emergency Power Output is on all the time - so that I can connect important electrical loads permanently rather than having to plug them into the emergency circuit when there is a power cut? I thought there was a setting to do that somewhere, but can't find it.
37kW PV, 60 Solar Vacuum tubes, 27kW Wood Pellet Boiler, 20kWh Pylon battery via Sofar ME3000 inverter, 18kW ASHP, 9kW GSHP
VW e-golf, Tesla S P85D
c.270 vacuum tube small commercial heating system +200kW pellet heating system with 4000litre thermal store
VW e-golf, Tesla S P85D
c.270 vacuum tube small commercial heating system +200kW pellet heating system with 4000litre thermal store
Re: Sofar ME3000 Emergency output
There are two kinds of off-grid output on inverters: EPS and UPS.
If your inverter has a UPS output, it’ll work as you describe. However if your inverter has an EPS output it’ll only be powered when the grid is down. This is a function of the internal architecture of the inverter so not something that can be changed with a setting.
You can however rig up some contactors to switch your critical load from grid to EPS in the event of a power outage.
If your inverter has a UPS output, it’ll work as you describe. However if your inverter has an EPS output it’ll only be powered when the grid is down. This is a function of the internal architecture of the inverter so not something that can be changed with a setting.
You can however rig up some contactors to switch your critical load from grid to EPS in the event of a power outage.
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Re: Sofar ME3000 Emergency output
Im sure I remember seeing the setting somewhere that allows it to be configured as either, but can't remember where it is in the settings.
37kW PV, 60 Solar Vacuum tubes, 27kW Wood Pellet Boiler, 20kWh Pylon battery via Sofar ME3000 inverter, 18kW ASHP, 9kW GSHP
VW e-golf, Tesla S P85D
c.270 vacuum tube small commercial heating system +200kW pellet heating system with 4000litre thermal store
VW e-golf, Tesla S P85D
c.270 vacuum tube small commercial heating system +200kW pellet heating system with 4000litre thermal store
Re: Sofar ME3000 Emergency output
No, it's just an eps so you need to use a change over contactor on it. Note that means the supply will be interupted on change over.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
Re: Sofar ME3000 Emergency output
Thats a shame - I was planning to put non-interuptible loads onto it like the pellet boiler. Thanks for the confirmation. BTW, how is your double-ME3000 setup working? I've just bought an extra one, so I'm planning to get a dual-inverter system running like yours
37kW PV, 60 Solar Vacuum tubes, 27kW Wood Pellet Boiler, 20kWh Pylon battery via Sofar ME3000 inverter, 18kW ASHP, 9kW GSHP
VW e-golf, Tesla S P85D
c.270 vacuum tube small commercial heating system +200kW pellet heating system with 4000litre thermal store
VW e-golf, Tesla S P85D
c.270 vacuum tube small commercial heating system +200kW pellet heating system with 4000litre thermal store
Re: Sofar ME3000 Emergency output
You still can put your pellet boiler on it! You just need to implement a pair of contactors!ivan wrote: ↑Sun Dec 15, 2024 1:57 pm Thats a shame - I was planning to put non-interuptible loads onto it like the pellet boiler. Thanks for the confirmation. BTW, how is your double-ME3000 setup working? I've just bought an extra one, so I'm planning to get a dual-inverter system running like yours
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Re: Sofar ME3000 Emergency output
The change over with the required contractor is automatic and very quick, info is in the Sofar manual, in fact you can specify the speed of switchover.Stinsy wrote: ↑Sun Dec 15, 2024 2:49 pmYou still can put your pellet boiler on it! You just need to implement a pair of contactors!ivan wrote: ↑Sun Dec 15, 2024 1:57 pm Thats a shame - I was planning to put non-interuptible loads onto it like the pellet boiler. Thanks for the confirmation. BTW, how is your double-ME3000 setup working? I've just bought an extra one, so I'm planning to get a dual-inverter system running like yours
18.7kW PV > 110MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 30MWh generated
6 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 520 m3
Ripple 6.6kW Wind + 4.5kW PV > 30MWh generated
6 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 520 m3
Re: Sofar ME3000 Emergency output
Wonder if it would be fast enough to fool the boiler
37kW PV, 60 Solar Vacuum tubes, 27kW Wood Pellet Boiler, 20kWh Pylon battery via Sofar ME3000 inverter, 18kW ASHP, 9kW GSHP
VW e-golf, Tesla S P85D
c.270 vacuum tube small commercial heating system +200kW pellet heating system with 4000litre thermal store
VW e-golf, Tesla S P85D
c.270 vacuum tube small commercial heating system +200kW pellet heating system with 4000litre thermal store
Re: Sofar ME3000 Emergency output
Ivan,
Do you know the minimum critical power interrupt duration is for the boiler ? If the switch over is too slow can you bridge the gap with an inline capacitor on the boiler side of the circuit ?
Moxi
Do you know the minimum critical power interrupt duration is for the boiler ? If the switch over is too slow can you bridge the gap with an inline capacitor on the boiler side of the circuit ?
Moxi
Re: Sofar ME3000 Emergency output
Totally! With the boiler running switch off-and-on-again its FCU. I'd guess it'd be happy with anything under a second or two. The changeover contactor will be in the region of 0.1-0.2s!
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)