Richard77 wrote: Sat Jan 11, 2025 5:13 pm
Thanks Stinsy...

Will leave it to the spark to have a look when they get round to installing in a couple of weeks.

But I was correct in thinking that ideally there should have been 2 positive and 2 negative connectors on to connect the batteries in parallel?
I don't think "should" is the correct term. Some do. But they tend to be much smaller eg pylontech 4.8kWh packs. Your ones are much bigger so maybe they need to be individually terminated to a bus bar or similar for the sake of the cables/connectors...
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Richard77
Posts: 167
Joined: Thu Sep 19, 2024 3:26 pm

Re: Solar PV advice

#92

Post by Richard77 »

Sorry for the quick sketch and dodgy writing!

Image

Is that possible if there is enough room in the inverter for two of each cables?
Last edited by Richard77 on Sat Jan 11, 2025 5:31 pm, edited 1 time in total.
Richard77
Posts: 167
Joined: Thu Sep 19, 2024 3:26 pm

Re: Solar PV advice

#93

Post by Richard77 »

Stinsy wrote: Sat Jan 11, 2025 5:23 pm
Richard77 wrote: Sat Jan 11, 2025 5:13 pm
Thanks Stinsy...

Will leave it to the spark to have a look when they get round to installing in a couple of weeks.

But I was correct in thinking that ideally there should have been 2 positive and 2 negative connectors on to connect the batteries in parallel?
I don't think "should" is the correct term. Some do. But they tend to be much smaller eg pylontech 4.8kWh packs. Your ones are much bigger so maybe they need to be individually terminated to a bus bar or similar for the sake of the cables/connectors...
It's just that I noticed on the similar specced fogstar models they had two of each.


Image
Richard77
Posts: 167
Joined: Thu Sep 19, 2024 3:26 pm

Re: Solar PV advice

#94

Post by Richard77 »

Thanks for the info guys...

I've got my head around the power distribution posts/busbar box now.

I think that's what will be needed as I can't imagine there being room to be able to squeeze 2x 35mm² cables into the SunSynk 8kw inverter for each of the positive and negative. From pics/videos looks like it's a tight fit to push one up there nevermind 2!
Marcus
Posts: 285
Joined: Mon Nov 08, 2021 6:25 pm

Re: Solar PV advice

#95

Post by Marcus »

Iirc you're using a 12kw inverter?

That's 250A going on 300A when the battery is low. Personally, I'd avoid daisy chaining batteries at that current anyway. I'd run both batteries direct to the inverter if at all possible, especially if the cables are only 35mm2. If you have to combine on an external post, I'd consider getting 70mm2 for the link to the inverter.
450W hydro-electric
5110W pv
1.3kw Wt2 - not yet producing
6kWh lead acid - maybe 1kwh useable
LiMnCo battery made from 2nd hand hybrid car modules 3.6kwh nominal 24v.
300lt hot water tank and two storage heaters
ASHP Grant Aerona 3 10.5kw and UFH
Richard77
Posts: 167
Joined: Thu Sep 19, 2024 3:26 pm

Re: Solar PV advice

#96

Post by Richard77 »

Marcus wrote: Sat Jan 11, 2025 8:45 pm Iirc you're using a 12kw inverter?

That's 250A going on 300A when the battery is low. Personally, I'd avoid daisy chaining batteries at that current anyway. I'd run both batteries direct to the inverter if at all possible, especially if the cables are only 35mm2. If you have to combine on an external post, I'd consider getting 70mm2 for the link to the inverter.
Hi Marcus...

Thanks for the suggestions.

It's only the 8kw SunSynk. Couldnt get dno to approve the 12kw. They approved the 8kw with an export limit of 6kw.
Richard77
Posts: 167
Joined: Thu Sep 19, 2024 3:26 pm

Re: Solar PV advice

#97

Post by Richard77 »

If I go the post route and use 70mm² to the inverter, I suppose the 2x 35mm² would have originally fitted. So wouldn't need to go down the post route in the first place.

I really could do with finding out what size cable physically the 8kw SunSynk can take thickness wise. :whako: (seems it's 70mm²)

Update edit: maybe 2x 35mm² will fit.

Image

What's everyone's thoughts on DC isolator between battery and inverter? I'm sure I read somewhere they are not recommended any longer.
MrPablo
Posts: 292
Joined: Mon Oct 17, 2022 1:26 pm

Re: Solar PV advice

#98

Post by MrPablo »

A fused isolator such as NH1 fuses in a Frankenstein style enclosure should be used between battery and inverter.
I mention NH1 as the more usual NH00 might not go up to the current rating you'll need.

Alternatively you could just have a fuse and a separate isolator, but the combo units are pretty compact.
Ideally you'd want a fuse per battery pack, I'm not sure if there's anything built into the enclosures you have.

The dc isolators that tend to not be recommended are for solar, I think it's because breaking a high voltage DC arc is not always straightforward. As a result, there's more risk of things going wrong.
10x 405W JA Solar panels (4.05kWp) @ 5 degrees
3x 405W Longi panels (1.22kWp) @ 90 degrees
16.5kWh DIY LifePo4 battery
Solis inverter/charger
0.6kW Ripple WT
64kWh Kia E-Niro
Richard77
Posts: 167
Joined: Thu Sep 19, 2024 3:26 pm

Re: Solar PV advice

#99

Post by Richard77 »

MrPablo wrote: Sat Jan 11, 2025 9:47 pm A fused isolator such as NH1 fuses in a Frankenstein style enclosure should be used between battery and inverter.
I mention NH1 as the more usual NH00 might not go up to the current rating you'll need.

Alternatively you could just have a fuse and a separate isolator, but the combo units are pretty compact.
Ideally you'd want a fuse per battery pack, I'm not sure if there's anything built into the enclosures you have.

The dc isolators that tend to not be recommended are for solar, I think it's because breaking a high voltage DC arc is not always straightforward. As a result, there's more risk of things going wrong.
Thanks MrPablo :xl:
User avatar
Colin Deng
Posts: 211
Joined: Mon Nov 21, 2022 8:33 am

Re: Solar PV advice

#100

Post by Colin Deng »

Parallel connection should be like this
Sorry for not answer in time

Got a busy weekend :oO:
Image