Richard77 wrote: Tue Jan 21, 2025 5:20 pm
AGT wrote: Tue Jan 21, 2025 5:15 pm 35mm2 meter tails from electrical wholesalers?
They might hire out crimping tools too?
I might just buy one... Seen some on eBay for about £23, hydraulic ones. Don't look too bad.

Yeah think I'm gonna go 35mm² everywhere and 200A/250A (inverter max discharge/charge 190A) fuses in the disconnect switch.

And buy the correct sized lugs for every connection.
M6 for inverter
M10 for fused disconnect.
M8 or M10 for bus bar box or whatever I end up buying.

And make up my own cables.
Good man, I like to draw up a line diagram to keep me right. I personally use a hammer crimper but that's just something I like. Do a pull test on every connection. I always go round twice when nipping up lugs to allow the metal to bed into its new torque setting. I don't use a torque wrench though but it's maybe worth doing? Looking forward to the pics!
15kW PV SE, VI, HM, EN
42kWh LFPO4 storage
7kW ASHP
200ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit trees
AGT
Posts: 1080
Joined: Sat Jan 29, 2022 11:26 am

Re: Solar PV advice

#152

Post by AGT »

Some colour coded insulating tape or heat shrink over the crimp also helps tidy things up.
AGT
Posts: 1080
Joined: Sat Jan 29, 2022 11:26 am

Re: Solar PV advice

#153

Post by AGT »

Oh and make sure you push down the crimp onto the cable as you press the crimping tool, sometimes they have a tendency to move slightly
Richard77
Posts: 188
Joined: Thu Sep 19, 2024 3:26 pm

Re: Solar PV advice

#154

Post by Richard77 »

Nice one for all the advice... Much appreciated.

I suppose I'll need some wire strippers and cutters too to make it seem like I know what I'm doing rather than a Stanley knife!
Richard77
Posts: 188
Joined: Thu Sep 19, 2024 3:26 pm

Re: Solar PV advice

#155

Post by Richard77 »

Ordered....
Image
AGT
Posts: 1080
Joined: Sat Jan 29, 2022 11:26 am

Re: Solar PV advice

#156

Post by AGT »

I use a Stanley knife, you get to know where to score to, and then you can peel the insulation back to the score to get a clean line..
User avatar
Stinsy
Posts: 3207
Joined: Wed Jun 02, 2021 1:09 pm

Re: Solar PV advice

#157

Post by Stinsy »

Richard77 wrote: Tue Jan 21, 2025 6:14 pm Nice one for all the advice... Much appreciated.

I suppose I'll need some wire strippers and cutters too to make it seem like I know what I'm doing rather than a Stanley knife!
While you can get tools such as this https://amzn.eu/d/8SIUK4N, a Stanley knife will do a perfectly good job. Cable sheers might be a wise investment though, something like this: https://amzn.eu/d/aB43wN6 (other brands are available, I like knipex though).
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Richard77
Posts: 188
Joined: Thu Sep 19, 2024 3:26 pm

Re: Solar PV advice

#158

Post by Richard77 »

Stanley knife it is then... Thanks :xl:

Thanks for the links Stinsy
Richard77
Posts: 188
Joined: Thu Sep 19, 2024 3:26 pm

Re: Solar PV advice

#159

Post by Richard77 »

Would a 400A Mersen NH2 3 pole be ok to use instead of a mersen 250A NH1 2 pole?

Found one cheaper than the NH1 with 400A fuses included.

Or would overspeccing by that much cause issues?

I know I would only use 2 of the 3 poles and only need upto 250A not 400A but are there any negatives? Can it cause any damage overspeccing?
User avatar
Fintray
Posts: 1682
Joined: Mon May 31, 2021 6:37 pm
Location: Aberdeenshire

Re: Solar PV advice

#160

Post by Fintray »

The fuse current capacity needs to be rated in relation to the current capacity of the cable .