I see...
So it wouldn't be wise to have 2x 35mm² that are rated for 240A with a fuse that is rated 400A even though it would only use less than 200A (battery max discharge/charge is 200A and inverter is max charge/discharge 190A).
It would be good practice to spec the cables to be capable of carrying 400A just in case, so 70mm² (485A)?