Upgrade a FIT/MCS PV+ to Hybrid PV + batt + 2nd systerm!
Upgrade a FIT/MCS PV+ to Hybrid PV + batt + 2nd systerm!
Existing is a 15 panel 2 strings of 265 watt (3975watt into a 3.6kW Power One inverter 2012) Close to due south facing roof at40 degree pitch.
Thinking of upgrade to 11 new 560watt panels, 7 panels of 2 unequal strings = 3920 watt to keep exising fit with a new 3.6kW Hybrid inverter and
battery pack of at least 10Kwh.
4 remaining new panels of 2240watt into a single string 2.0 kW inverter with isolaters and a new generation meter.
Upgrade through G99 with a request to add additional 2 kW of export to existing. (6 kW export in total)
Any thoughts advice and recommendations welcome!
Thinking of upgrade to 11 new 560watt panels, 7 panels of 2 unequal strings = 3920 watt to keep exising fit with a new 3.6kW Hybrid inverter and
battery pack of at least 10Kwh.
4 remaining new panels of 2240watt into a single string 2.0 kW inverter with isolaters and a new generation meter.
Upgrade through G99 with a request to add additional 2 kW of export to existing. (6 kW export in total)
Any thoughts advice and recommendations welcome!
Re: Upgrade a FIT/MCS PV+ to Hybrid PV + batt + 2nd systerm!
Good idea. However you'd benefit from putting panels on your north-facing roof too.Comper wrote: ↑Wed Jan 29, 2025 5:16 pm Existing is a 15 panel 2 strings of 265 watt (3975watt into a 3.6kW Power One inverter 2012) Close to due south facing roof at40 degree pitch.
Thinking of upgrade to 11 new 560watt panels, 7 panels of 2 unequal strings = 3920 watt to keep exising fit with a new 3.6kW Hybrid inverter and
battery pack of at least 10Kwh.
4 remaining new panels of 2240watt into a single string 2.0 kW inverter with isolaters and a new generation meter.
Upgrade through G99 with a request to add additional 2 kW of export to existing. (6 kW export in total)
Any thoughts advice and recommendations welcome!
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
-
- Posts: 229
- Joined: Fri Mar 11, 2022 7:48 pm
- Location: Lincolnshire
Re: Upgrade a FIT/MCS PV+ to Hybrid PV + batt + 2nd systerm!
+1 to that. I’m getting about 50% on a north facing roof over a year. With the price of panels being so low it makes sense to do so - IMOStinsy wrote: ↑Wed Jan 29, 2025 5:19 pmGood idea. However you'd benefit from putting panels on your north-facing roof too.Comper wrote: ↑Wed Jan 29, 2025 5:16 pm Existing is a 15 panel 2 strings of 265 watt (3975watt into a 3.6kW Power One inverter 2012) Close to due south facing roof at40 degree pitch.
Thinking of upgrade to 11 new 560watt panels, 7 panels of 2 unequal strings = 3920 watt to keep exising fit with a new 3.6kW Hybrid inverter and
battery pack of at least 10Kwh.
4 remaining new panels of 2240watt into a single string 2.0 kW inverter with isolaters and a new generation meter.
Upgrade through G99 with a request to add additional 2 kW of export to existing. (6 kW export in total)
Any thoughts advice and recommendations welcome!
Re: Upgrade a FIT/MCS PV+ to Hybrid PV + batt + 2nd systerm!
Is that with another inverter or just adding to existing?
Re: Upgrade a FIT/MCS PV+ to Hybrid PV + batt + 2nd systerm!
You can do what you like!
I’d suggest having a FiT inverter going through the FiT meter then have a hybrid inverter with 2x MPPTs one with a single string on your south roof and 2x strings on your North roof paralleled up into the 2nd MPPT.
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Re: Upgrade a FIT/MCS PV+ to Hybrid PV + batt + 2nd systerm!
Without wanting to derail the original thread I have a WNW facing large roof that has zero shading issues and should fit 16 panels which would be an interesting addition to 8 ESE facing panels on the other side of the ridge....
Re: Upgrade a FIT/MCS PV+ to Hybrid PV + batt + 2nd systerm!
Go for it!
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Re: Upgrade a FIT/MCS PV+ to Hybrid PV + batt + 2nd systerm!
I would second that my 3.6kWp West array does very well for us.
Moxi
Moxi
Re: Upgrade a FIT/MCS PV+ to Hybrid PV + batt + 2nd systerm!
Hiya. I think your plan is probably best, if you plan on adding that DC side battery.Comper wrote: ↑Wed Jan 29, 2025 5:16 pm Existing is a 15 panel 2 strings of 265 watt (3975watt into a 3.6kW Power One inverter 2012) Close to due south facing roof at40 degree pitch.
Thinking of upgrade to 11 new 560watt panels, 7 panels of 2 unequal strings = 3920 watt to keep exising fit with a new 3.6kW Hybrid inverter and
battery pack of at least 10Kwh.
4 remaining new panels of 2240watt into a single string 2.0 kW inverter with isolaters and a new generation meter.
Upgrade through G99 with a request to add additional 2 kW of export to existing. (6 kW export in total)
Any thoughts advice and recommendations welcome!
You could run it all through a new and larger inverter, and get the FiT apportioned. That's what I've done. But .... if the battery is DC side, then for FiTs you'll need to change the TGM for a bi-directional meter, and because of battery losses, you'll end up with a small net loss to generation (and FiTs), if charging the battery from the grid in winter (as I do). Eg, if you charged 10kWh at night, the TGM would record -10, then when you use that and get say 8kWh out, it will record +8, and the net reading will have gone down 2.
Edit - Sorry, misread, I see the DC battery is on the FiT string. In that case better to put it all through one inverter*, or go with an AC side battery, and keep the old TGM, and no net losses.
*If you have a DC side battery, then you'll be able to have a lower powered inverter, if the DNO won't give you a higher export limit. My 3.68kW inverter can also redirect upto 5kW DC to the batts, so no clipping from the 6.7kWp PV, so long as there is space in the batts.
8.7kWp PV [2.12kWp SSW + 4.61kWp ESE PV + 2.0kWp WNW PV]
Two BEV's.
Two small A2A heatpumps.
20kWh Battery storage.
Two BEV's.
Two small A2A heatpumps.
20kWh Battery storage.
Re: Upgrade a FIT/MCS PV+ to Hybrid PV + batt + 2nd systerm!
Many thanks for your comments and advice.
Regarding east west and north elevations they are not pracical due to valleys and smaller roof areas.
I thought upgrading existing to as close as original would give greater uplift due to newer panels being considerably more efficient and my older panels may have lost 10% + or - over13 years.
One question can anyone identify this mounting system below as hoping to reuse the mounting brackets and attach new rails and clamps.
Regarding east west and north elevations they are not pracical due to valleys and smaller roof areas.
I thought upgrading existing to as close as original would give greater uplift due to newer panels being considerably more efficient and my older panels may have lost 10% + or - over13 years.
One question can anyone identify this mounting system below as hoping to reuse the mounting brackets and attach new rails and clamps.