AGT wrote: ↑Sat Mar 15, 2025 6:57 am
Difficult to see, I would run a 4mm2 cable from the battery case to the inverter case, the flex with the L,N,E conductors are earthing the inverter the 4mm2 is the size of cable if not mechanically protected
There should be continuity from the E in the flex to the case so you are linking all the metal work together to be at the same potential- same potential no likelihood of a shock
pudding wrote: ↑Sat Mar 15, 2025 7:37 am
First pic inside the inverter, looks like the earth is connected, can see the bare solid copper going to the E screw terminal far right. For the outside, that for your battery earth connection, might have to make up your own cable for that one.
Thanks guys for taking a look.
Unfortunately, the batteries aren't going in until after the garage doors go on and floor done properly. Looking at April 8th for the garage doors.
I have some earth cable that I will have to put some small lugs on to connect the batteries to the inverter when the time comes. Bottom of inverter case ----> battery 1 ------> battery 2.
Sorry if the picture was misleading and making you think the batteries were installed:
When looking at the inside in preparation of battery install,
my concern was that the inverter wasn't earthed properly?
So only having an earth wire plugged into the earth grid connector in the inverter that eventually finds it's way back to the house water/gas pipes (through isolators, fuseboxes, etc) is ok?
When I saw in the manual about earth connection (mandatory) at the bottom of inverter case, alarm bells triggered!