15 kVa transformer good for what power?

Andy
Posts: 487
Joined: Sun Aug 29, 2021 12:16 pm

15 kVa transformer good for what power?

#1

Post by Andy »

After Joe’s post I have a question that has been bothering me for a while. We are running off a 15kVA transformer ( reading from the plate) powering three houses. I have also had the house fuse upgraded to 80A single phase.

Now I have my zappi set to limit incoming Amps to 60 despite the 80A fuse in order to be neighbourly. 60 amps is about 13.8 kW depending on voltage. 15kVa is about 13.5kW at 90power factor. So already I am supposedly using almost all the capacity of the transformer. So if I am charging batteries and the car and hitting these limits for 4 hours, is this a problem in reality? Both neighbours are currently very light users of the grid but this won’t always be the case.

I’m sorry I can’t remember who mentioned recently, maybe Stinsy, that DNO can demand a 60A limit for sustained loads. What happens if all three properties start doing this?
Last edited by Andy on Wed Jan 12, 2022 10:24 pm, edited 1 time in total.
User avatar
Joeboy
Posts: 7795
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: 15 kVa transformer god for what power?

#2

Post by Joeboy »

It takes a lot to melt the insulation in a transformer Andy. Although I have seen and smelled it. Even heard the pop. I'd be asking for a transformer upgrade by the dno? Can't do any harm?
19.7kW PV SE, VI, HM, EN & DW
Ripple 7kW WT & Gen to date 19MWh
42kWh LFPO4 storage
95kWh Heater storage
12kWh 210ltr HWT.
73kWh HI5
Deep insulation, air leak ct'd home
Zoned GCH & Hive 2
WBSx2
Low energy bulbs
Veg patches & fruit trees
Andy
Posts: 487
Joined: Sun Aug 29, 2021 12:16 pm

Re: 15 kVa transformer god for what power?

#3

Post by Andy »

I’m not sure how that’d go down well as I got it upgraded a few years ago because it was over voltage 😂

I guess if the neighbours ever get an electric car I’ll let them know how much I am using.
User avatar
nowty
Posts: 5575
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: 15 kVa transformer good for what power?

#4

Post by nowty »

Probably depends somewhat on the ambient temperature so in winter you can probably draw that little bit extra. ;)
16.9kW PV > 107MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 22MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
User avatar
Stinsy
Posts: 2640
Joined: Wed Jun 02, 2021 1:09 pm

Re: 15 kVa transformer good for what power?

#5

Post by Stinsy »

If I were you I’d keep an eye on voltage sag. Ie measure voltage with only trivial loads then charge your car, run your hob, etc., and measure the voltage again.

If the voltage drops too low you can complain to the DNO, but I believe they are only required to keep voltage between 216-253V so there is a lot of leeway,
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Andy
Posts: 487
Joined: Sun Aug 29, 2021 12:16 pm

Re: 15 kVa transformer good for what power?

#6

Post by Andy »

The voltage sag isn’t too bad. It’s running between 230 and 240v fairly consistently now. I lose about 3v when maxed out.

We were hitting 256v on windy sunny days before the transformer got replaced.
User avatar
Stinsy
Posts: 2640
Joined: Wed Jun 02, 2021 1:09 pm

Re: 15 kVa transformer good for what power?

#7

Post by Stinsy »

Don't worry then!
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Oliver90owner
Posts: 376
Joined: Wed Jun 16, 2021 3:48 pm

Re: 15 kVa transformer good for what power?

#8

Post by Oliver90owner »

15kVA is about 12kW resistive. I suspect that rating is a conservative value for each phase and each dwelling is fed from a separate phase.

Transformers do not like nearly 100% loading on one phase with little or nothing on the other legs, hence the conservative rating is very likely.

The transformers have different tappings for voltage selection and is a minor adjustment. It does not affect the kVA rating.
Tinbum
Posts: 1073
Joined: Mon May 31, 2021 9:55 pm

Re: 15 kVa transformer good for what power?

#9

Post by Tinbum »

I don't think it will be per phase,

Our 100KVA transformer plate.
Image
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
Andy
Posts: 487
Joined: Sun Aug 29, 2021 12:16 pm

Re: 15 kVa transformer good for what power?

#10

Post by Andy »

Stinsy wrote: Thu Jan 13, 2022 10:57 amDon't worry then!
Roger :) I am a perpetual worrier and rule follower that constantly gets me in trouble compared to people I know who just crack on haha
Post Reply