Another fellow camelot member has been using a second Sofar ME3000SP in "Timed Mode" in order to make use of the high export prices between 4pm and 8pm over the summer months when their batteries are full almost everyday. They have given me permission to post it here as it might help others who want to time shift their export. There have been several units coming up on fleebay for as little as £350 as some installers seem to be persuading existing users to swap them for LUX units which might now have some sort of Octopus API integration. Maybe that is the way to go I don't know.
Its possible to do fancy things in passive mode with the ME3000SP but that takes extra hardware and programming skills. This just uses the existing work modes across two ME3000SP units.
So the trick is to have two units sharing the same battery, ensure the clocks on each unit are as close to each other as possible and not to use any CT clamps on the second unit which will be used as a dumb unit.
First unit is installed as a normal install with the CT clamps in place but run in "Time of Use" mode with the 4pm to 8pm slot (or other peak time period) set to charge at zero watts so for that time period it just says in standby mode. The rest of the time it operates as normal, therefore charging the battery with excess solar or supplying power to the house to minimise imports.
Second unit is run as a dumb unit with no cable clamps. If you use "Timed" mode, which is essentially designed as a test mode, you can set it to discharge between 4pm and 8pm (or other peak time period matching the first unit) to get the max export price rates.
Results, the screenshots below have been taken from their online Octopus account.
Octopus Outgoing Export Price Rates (the rates for last nights run were actually higher and especially for 5pm to 7pm)
You can clearly see the additional time shifted peak between 5pm and 7.00pm
Their import was practically nothing all day (note different scale)
Forced Discharge Time Shifting with Octopus Agile Outgoing
Forced Discharge Time Shifting with Octopus Agile Outgoing
Last edited by nowty on Sun Aug 01, 2021 4:35 pm, edited 2 times in total.
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Re: Forced Discharge Time Shifting with Octopus Agile Outgoing
Impressive stuff.
Tesla Model 3 Performance
Oversees an 11kWp solar array at work
Oversees an 11kWp solar array at work
Re: Forced Discharge Time Shifting with Octopus Agile Outgoing
I doubt Octopus thought this was ever ever going to be a reality with their Agile price formulas. They put in two protections, first, that Agile Outgoing will never go negative and the second that Agile import will be capped at 35p. Bet they never, ever thought the outgoing price would be in the hundreds of pence day after day.
This afternoon someone on here has been charging their battery bank at 35p / kWh from the grid which you would think was crazy. But at 6pm they are going to unleash those batteries onto the grid to be paid up to a peak price of 220p / kWh. Tomorrows Agile Outgoing is peaking even higher at 240p / kWh.
This afternoon someone on here has been charging their battery bank at 35p / kWh from the grid which you would think was crazy. But at 6pm they are going to unleash those batteries onto the grid to be paid up to a peak price of 220p / kWh. Tomorrows Agile Outgoing is peaking even higher at 240p / kWh.
Last edited by nowty on Tue Sep 14, 2021 6:10 pm, edited 1 time in total.
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Re: Forced Discharge Time Shifting with Octopus Agile Outgoing
I wish my next door neighbour was on Octopus outgoing. We could do a once-a-day battery swap to charge at 5p and discharge at 240p!
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
3x 380W JA Solar panels (1.14kWp)
5x 2.4kWh Pylontech batteries (12kWh)
LuxPower inverter/charger
(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
-
- Posts: 63
- Joined: Mon Aug 23, 2021 12:31 pm
Re: Forced Discharge Time Shifting with Octopus Agile Outgoing
It would be very easy to this in passive mode without needing another unit but I guess it's good to have a spare.
The Python to do it is below and in my project on github - just need to add a few lines to call that and later switch it back to auto.
def set_charge(self, charge=3000):
""" Set charge value."""
ret_status = True
message = write_passive_register(slave_id=self.slave_id,
address=self.CHARGE,
value=charge)
try:
response = rtu.send_message(message, self.serial_port)
except:
ret_status = False
response = 0
return ret_status, response
def set_auto(self):
""" Switch inverter to AUTO."""
ret_status = True
message = write_passive_register(slave_id=self.slave_id,
address=self.AUTO,
value=0)
try:
response = rtu.send_message(message, self.serial_port)
except:
ret_status = False
response = 0
return ret_status, response
The Python to do it is below and in my project on github - just need to add a few lines to call that and later switch it back to auto.
def set_charge(self, charge=3000):
""" Set charge value."""
ret_status = True
message = write_passive_register(slave_id=self.slave_id,
address=self.CHARGE,
value=charge)
try:
response = rtu.send_message(message, self.serial_port)
except:
ret_status = False
response = 0
return ret_status, response
def set_auto(self):
""" Switch inverter to AUTO."""
ret_status = True
message = write_passive_register(slave_id=self.slave_id,
address=self.AUTO,
value=0)
try:
response = rtu.send_message(message, self.serial_port)
except:
ret_status = False
response = 0
return ret_status, response
65 x Ø58mm SunnPro/Gledhill 450l
Solis Mini 4G 3kW/Sharp ND210/2.94kWp
SB1600/Sharp ND220/1.76kWp
SB1600/Kinve 235/2.115kWp
Dean Forge Croft Clearburn 11kW
SoFar ME3000/Pylontech US2000/19.2kWh
Ecodan 11kW HP
MG4
Zoe R135
PVOutput
Solis Mini 4G 3kW/Sharp ND210/2.94kWp
SB1600/Sharp ND220/1.76kWp
SB1600/Kinve 235/2.115kWp
Dean Forge Croft Clearburn 11kW
SoFar ME3000/Pylontech US2000/19.2kWh
Ecodan 11kW HP
MG4
Zoe R135
PVOutput
Re: Forced Discharge Time Shifting with Octopus Agile Outgoing
Or even a neighbour AC interconnector if you are both on the same phase (almost certainly not legal). Or even if you were not you could have a communal battery and a DC interconnector.
The mind boggles.
Last edited by nowty on Wed Sep 15, 2021 1:10 pm, edited 1 time in total.
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Re: Forced Discharge Time Shifting with Octopus Agile Outgoing
Looks like the fellow Camelot member increased the discharge as the price increased.
6.4 kWh import at 35p = 224p
3.7 kWh export at an approx average of 200p = 740p
I suspect today will be a re-run.
6.4 kWh import at 35p = 224p
3.7 kWh export at an approx average of 200p = 740p
I suspect today will be a re-run.
18.7kW PV > 109MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Ripple 6.6kW Wind + 4.5kW PV > 26MWh generated
5 Other RE Coop's
105kWh EV storage
60kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 510 m3
Re: Forced Discharge Time Shifting with Octopus Agile Outgoing
I'm using your Github code with Node-RED and am new to Python but do a bit with Arduino's etc.greentangerine wrote: ↑Tue Sep 14, 2021 6:19 pm It would be very easy to this in passive mode without needing another unit but I guess it's good to have a spare.
The Python to do it is below and in my project on github - just need to add a few lines to call that and later switch it back to auto.
def set_charge(self, charge=3000):
""" Set charge value."""
ret_status = True
message = write_passive_register(slave_id=self.slave_id,
address=self.CHARGE,
value=charge)
try:
response = rtu.send_message(message, self.serial_port)
except:
ret_status = False
response = 0
return ret_status, response
def set_auto(self):
""" Switch inverter to AUTO."""
ret_status = True
message = write_passive_register(slave_id=self.slave_id,
address=self.AUTO,
value=0)
try:
response = rtu.send_message(message, self.serial_port)
except:
ret_status = False
response = 0
return ret_status, response
Is their a way to set the time on the ME3000 via Python and Node-RED?
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW