new member with new battery
Re: new member with new battery
Other option is that CT's are the wrong way round i.e. PV on Grid and vice versa.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 135kWh Rolls batteries, 52kWh Growatt storage GBLI 6532, 66kWh Pylontech US3000C, 43kWh DIY, Sofar ME3000's, Brosley wood burner and 250lt DHW
Re: new member with new battery
Photos can 'explain' a system more easily than words in many cases.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 135kWh Rolls batteries, 52kWh Growatt storage GBLI 6532, 66kWh Pylontech US3000C, 43kWh DIY, Sofar ME3000's, Brosley wood burner and 250lt DHW
-
- Posts: 662
- Joined: Mon Mar 21, 2022 7:37 pm
Re: new member with new battery
Yes and I suspect someone has changed something remotely. My thought was the maximum charge voltage for the battery was being exceeded but with the sunniest day so far the fault has not appeared.
I hope I have attached a screenshot of the fault and the text does not match anything in the fault section of the manual exactly.
Also a photo of the units side by side


BTW thanks for the help all, sorry if I offended with my remark about FIT payments
I hope I have attached a screenshot of the fault and the text does not match anything in the fault section of the manual exactly.
Also a photo of the units side by side


BTW thanks for the help all, sorry if I offended with my remark about FIT payments
Morso S11
FIT
4kW panels facing WSW
Solarmax 4200S
Non FIT
disparate string
1.75kW facing SSE
0.85kW facing NE
2.6kW facing WSW
Sunsynk 3.6kW inverter
Storage
10.4kWh GLS lithium phosphate battery
FIT
4kW panels facing WSW
Solarmax 4200S
Non FIT
disparate string
1.75kW facing SSE
0.85kW facing NE
2.6kW facing WSW
Sunsynk 3.6kW inverter
Storage
10.4kWh GLS lithium phosphate battery
-
- Posts: 2288
- Joined: Wed Jun 02, 2021 6:10 pm
Re: new member with new battery
there's a very British prejudice against talking about money in any way, although some here are very (and unusually) open about the financial implications of their own renewables and even about their investments and pension plan structures.
I wasn't surprised by the response...
A
2.0 kW/4.62 MWh pa in Ripples, 4.5 kWp W-facing pv, 9.5 kWh Givenergy batt
30 solar thermal tubes, 2MWh pa in Stockport, plus Congleton and Kinlochbervie Hydros,
Most travel by bike, walking or bus/train. Veg, fruit - and Bees!
30 solar thermal tubes, 2MWh pa in Stockport, plus Congleton and Kinlochbervie Hydros,
Most travel by bike, walking or bus/train. Veg, fruit - and Bees!
Re: new member with new battery
Well played.openspaceman wrote: ↑Tue Mar 22, 2022 5:57 pm Yes and I suspect someone has changed something remotely. My thought was the maximum charge voltage for the battery was being exceeded but with the sunniest day so far the fault has not appeared.
I hope I have attached a screenshot of the fault and the text does not match anything in the fault section of the manual exactly.
Also a photo of the units side by side
BTW thanks for the help all, sorry if I offended with my remark about FIT payments

15kW PV SE, VI, HM, EN
42kWh LFPO4 storage
73kWh V2H EV
7kW ASHP
200ltr HWT.
3G
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit
42kWh LFPO4 storage
73kWh V2H EV
7kW ASHP
200ltr HWT.
3G
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit
Re: new member with new battery
That code does not mean much to me either.
It might be a temporary thing, coming out of Winter where the battery needs a few full charge / discharge cycles to balance up the cells, then its ok. New Pylontech batteries sometimes give a high / low voltage cell error but it more of a warning than a shutdown fault and usually clears after a few cycles.
If its working for you this evening without any intervention, just keep an eye on it.
It might be a temporary thing, coming out of Winter where the battery needs a few full charge / discharge cycles to balance up the cells, then its ok. New Pylontech batteries sometimes give a high / low voltage cell error but it more of a warning than a shutdown fault and usually clears after a few cycles.
If its working for you this evening without any intervention, just keep an eye on it.
19.6kW PV > 114MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 34MWh generated
7 Other RE Coop's
105kWh EV storage
90kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 530 m3
Ripple 6.6kW Wind + 4.5kW PV > 34MWh generated
7 Other RE Coop's
105kWh EV storage
90kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 530 m3
Re: new member with new battery
I disagree, it may be a generational thing. Not particularly linked to Britishness in my life experience... shrugs. Regarding the gentle nudge it's nice to help others in how we've been doing it and hopefully they get more out of it.AE-NMidlands wrote: ↑Tue Mar 22, 2022 6:32 pmthere's a very British prejudice against talking about money in any way, although some here are very (and unusually) open about the financial implications of their own renewables and even about their investments and pension plan structures.
I wasn't surprised by the response...
A
15kW PV SE, VI, HM, EN
42kWh LFPO4 storage
73kWh V2H EV
7kW ASHP
200ltr HWT.
3G
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit
42kWh LFPO4 storage
73kWh V2H EV
7kW ASHP
200ltr HWT.
3G
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit
Re: new member with new battery
I just found the user manual for the battery, the nearest type of failure I can find is a simple comms failure between the inverter and the battery so check that the comms cable is connected properly, i.e. give it a wiggle or re-seat the connector.
Communication failure.
Communication loss between PCS and battery
Check if PCS and battery communication terminal is well connected.
Communication failure.
Communication loss between PCS and battery
Check if PCS and battery communication terminal is well connected.
19.6kW PV > 114MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 34MWh generated
7 Other RE Coop's
105kWh EV storage
90kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 530 m3
Ripple 6.6kW Wind + 4.5kW PV > 34MWh generated
7 Other RE Coop's
105kWh EV storage
90kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 530 m3
Re: new member with new battery
The battery should be telling the inverter what the max charge voltage is so shouldn't be exceeded. The error looks to be a problem of communication between battery and inverter.
nowty- i took too long to press the submit button while check the manual again!!
The instructions look awful- typical Chinese.
nowty- i took too long to press the submit button while check the manual again!!
The instructions look awful- typical Chinese.

85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 135kWh Rolls batteries, 52kWh Growatt storage GBLI 6532, 66kWh Pylontech US3000C, 43kWh DIY, Sofar ME3000's, Brosley wood burner and 250lt DHW
Re: new member with new battery
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 135kWh Rolls batteries, 52kWh Growatt storage GBLI 6532, 66kWh Pylontech US3000C, 43kWh DIY, Sofar ME3000's, Brosley wood burner and 250lt DHW