Re: SOFAR ME3000SP
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
Re: SOFAR ME3000SP
i will get the settings from the bmss
Re: SOFAR ME3000SP
Cheers Nowty,nowty wrote: ↑Mon Aug 12, 2024 10:44 amIts not Moxi, I have one.Moxi wrote: ↑Mon Aug 12, 2024 8:32 am I'm just wondering if the problem is the depth of discharge figure?
Looking at the screen you have said "I want to be able to discharge 80% of the battery" BUT what if the logic is written so that 80% discharge means only 20% of the battery is used ? so then the inverter tries to start charging a battery that's 80% full at 50Amps which fires up the overvault alarm as the BMS requires a lower amperage above the 80% point?
If you set the DoD to 20% will it then charge at 50 amps without fault?
I'm probably way off the mark but thought I would mention it.
Moxi
Only thing I can think of is drop the charge voltage down a touch to 58V or even 57V and see if that helps.
I had to ask as on my Solis its 20% and I would have felt silly if I hadn't mentioned it just in case.
Stay with it Grumpy, the forum hive mind doesn't often fail.
Moxi
Re: SOFAR ME3000SP
also my jk bmss have no communication to the sofar units
Re: SOFAR ME3000SP
Yes,
It looks as if you haven't changed your settings from default.
You have COV set at 3.6v which equates to 57.6v so the BMS will turn off at that voltage.
Your 'continued' charge current is 25A.
Your UTPR and UTP are also incorrect.
It looks as if you haven't changed your settings from default.
You have COV set at 3.6v which equates to 57.6v so the BMS will turn off at that voltage.
Your 'continued' charge current is 25A.
Your UTPR and UTP are also incorrect.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
Re: SOFAR ME3000SP
That explains it even more.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, 8kWh Growatt storage, 22 x US3000C Pylontech, Sofar ME3000's, Brosley wood burner and 250lt DHW
Re: SOFAR ME3000SP
thanks for reply
I have not changed my settings from default
would you know what they should be set to
thanks
I have not changed my settings from default
would you know what they should be set to
thanks
Re: SOFAR ME3000SP
My continued charge current is 25 amps
is this what the bms is set to receive and will not accept above that figure
does this mean i have to up the continued charge current figure
please advise
is this what the bms is set to receive and will not accept above that figure
does this mean i have to up the continued charge current figure
please advise
Re: SOFAR ME3000SP
You can see some recommended JK BMS settings (for LFP cells) here - https://off-grid-garage.com/my-settings/
These are a good starting point and should improve your experience.
These are a good starting point and should improve your experience.